Controllo inverter in Modbus RTU e pannello Weintek – Support Elsist https://support.elsist.biz/forums/topic/controllo-inverter-in-modbus-rtu-e-pannello-weintek/feed/ Fri, 30 Oct 2026 09:06:09 +0000 https://bbpress.org/?v=2.6.20 it-IT https://support.elsist.biz/forums/topic/controllo-inverter-in-modbus-rtu-e-pannello-weintek/#post-50669 Controllo inverter in Modbus RTU e pannello Weintek https://support.elsist.biz/forums/topic/controllo-inverter-in-modbus-rtu-e-pannello-weintek/#post-50669 Mon, 04 Nov 2019 09:03:49 +0000 Michele Avrei necessità di controllare 2 inverter in MODBUS RTU (RS-485) ed utilizzare un Pannello Weintek MT6050i connesso in MODBUS RTU collegando il tutto con la porta FIELDBUS del PLC SlimLine Compact.

Avreste indicazioni a riguardo, eventuali esempi?

]]>
https://support.elsist.biz/forums/topic/controllo-inverter-in-modbus-rtu-e-pannello-weintek/#post-50674 Rispondi a: Controllo inverter in Modbus RTU e pannello Weintek https://support.elsist.biz/forums/topic/controllo-inverter-in-modbus-rtu-e-pannello-weintek/#post-50674 Mon, 04 Nov 2019 09:11:31 +0000 Sergio Bertana Il Modbus RTU prevede un unico sistema master, quindi il pannello sarà master Modbus mentre sia gli inverter che lo SlimLine saranno slave Modbus.

Per quanto riguarda la connessione del panello Weintek allo SlimLine puoi guardare questo topic, per gli inverter devi riferirti alla documentazione relativa.

Tutti i dispositivi della rete Modbus dovranno comunicare con gli stessi parametri seriali (Lo SlimLine di default è 115200, e, 8), ed avere ognuno indirizzo di nodo diverso (LO slimLIne di default è 1). Sia i parametri di comunicazione seriale che l’indirizzo di nodo possono essere modificatio da pagina web.

]]>