Connessione pannello cMT-3072XH con PLC SE TM241 in ethernet – Support Elsist https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/feed/ Fri, 30 Oct 2026 08:35:34 +0000 https://bbpress.org/?v=2.6.20 it-IT https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-63992 Connessione pannello cMT-3072XH con PLC SE TM241 in ethernet https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-63992 Thu, 24 Feb 2022 16:47:57 +0000 TecGio Nella configurazione come da topic non riesco a fare comunicare il pannello con il PLC, continuo ad avere la finestra di pop up “Device no response”. Indirizzi IP e Subnet mask verificati.

- DATI DISPOSITIVI.
PLC = SE TM241
PANNELLO = cMT-3072XH
Programma Schneider Electric = Machine Expert (che ha sostituito SoMachine)

- IMPOSTAZIONI HMI / PLC
Locale HMI = modello = cMT-3072XH - stazione HMI=0 - Porta = 8000
provato anche "Supporta protocollo HMI ..." porta 8010
dispositivo = Schneider SoMachine M Series (Ethernet)
Dispositivo ID:286,V. 4.30, SOMACHINE_M_SERIER_ETHERNET e30

PLC I/F = Ethernet
IP: 192.168.34.78 Porta=1740 - Sorgente Porta n.1742
IP e SM verificati - PC e PLC comunicano bene
[v] Usa UDP
Stazione = 1
-- Importa Tag = ok - variabili corrette

Se inserisco su pannello la gestione di un BOOL pulsante o spia  si apre la finestra “Device no response”

– IMPOSTAZIONI MODBUS

Con dispositivo in tipo = Schneider MODBUS TCP/IP riesco a comunicare.

]]>
https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-64003 Rispondi a: Connessione pannello cMT-3072XH con PLC SE TM241 in ethernet https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-64003 Thu, 24 Feb 2022 16:49:29 +0000 Sergio Bertana Prova a disattivare l’accesso utente sul PLC.

Questa impostazione è da fare sul software Machine expert.

]]>
https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-64018 Rispondi a: Connessione pannello cMT-3072XH con PLC SE TM241 in ethernet https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-64018 Fri, 25 Feb 2022 12:53:59 +0000 TecGio dai Menu:

– in linea – sicurezza – disattiva gestione diritti utenti su dispositivo.

Funziona, grazie…

]]>
https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-68963 Rispondi a: Connessione pannello cMT-3072XH con PLC SE TM241 in ethernet https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-68963 Tue, 27 Dec 2022 11:39:15 +0000 Milosav I have used simulation mode, I have created symbol configuration in Machine Expert and export a data with right click on symbol configuration and choose an option Export Symbols to Vijeo Designer to create .xml file.

When I go to EasyBuilder Pro, a create a new device with Schneider SoMachine M Series. Then I go to option Import Tags, choose .xml file that I was previous created, I received message that tags was successfully imported, but there is no tags in Address option in EasyBuilder Pro I couldn’t find any tags.

What is a problem?

]]>
https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-68971 Rispondi a: Connessione pannello cMT-3072XH con PLC SE TM241 in ethernet https://support.elsist.biz/forums/topic/connessione-pannello-cmt-3072xh-con-plc-se-tm241-in-ethernet/#post-68971 Wed, 28 Dec 2022 10:05:07 +0000 Sergio Bertana When you work with PLC with simbolic addressing the imported TAGs are not displayed in the TAG list, they are directly visible in the variable selection inside the objects declaration.

Insert an object (As a Toggle button) on a page and when selet the relate variable choose User-defined tag.

]]>